i have a power tool that requires a 240-110 transformer ,i need help with which transformer i need to buy?
February 23rd, 2008 | by admin |mike r asked:
the power tool says max input 2.8 kva. do i need a 3kva transformer to run this tool or is a 3 kva transformer to big. can i buy a smaller 1 kva unit that will run the tool?
Question posted courtesy of: Valerie
the power tool says max input 2.8 kva. do i need a 3kva transformer to run this tool or is a 3 kva transformer to big. can i buy a smaller 1 kva unit that will run the tool?
Question posted courtesy of: Valerie











8 Responses to “i have a power tool that requires a 240-110 transformer ,i need help with which transformer i need to buy?”
By Alex B on Feb 25, 2008 | Reply
The max size transformer it is able to handle is 2.8 kva, so buy 2.7 or smaller. Definitely dont go over, it will burn your tool out.
By Just_gone on Feb 28, 2008 | Reply
3 kva. 1 kva will burn up.
I am a journeyman electrician (ret).
By JOHNNIE B on Feb 29, 2008 | Reply
No u need to go bigger a 3kva should be ok normally they should take a 50% over load for a short time.
By websterjdjr on Mar 1, 2008 | Reply
2.8 is MAX input anythang larger than that MAY burn up the tool why not be safe and buy the exact replacement transformer?
By Joe M on Mar 3, 2008 | Reply
240v is single-phase 2-pole.
110 is single-phase 1-pole.
‘Max input’ doesn’t make any sense though - it should be ‘maximum load’. If it is going to pull 2.8kva max (usually measured with a locked rotor) then you will need a 3kva to give you sufficient power.
You might want to post more details - or contact me with them, and I can try to help you (or contact the manufacturer and see if they recommend a specific transformer - or at least give you the specs to be looking for).
By turd on Mar 5, 2008 | Reply
Minimum to use is a 2.8kVA transformer - and it will run hot. This is going to be a MONSTER transformer though.
By tlbs101 on Mar 8, 2008 | Reply
You should get a transformer rated for a load that is larger than the actual load, so the transformer won’t burn up.
3 kVA is a good start. Something even larger would be a bit better, but those things are expensive when you start talking about 5 kVA and up. If you can afford a 5 kVA step-down transformer, I would get that.
.
By jairarodrguez on Mar 10, 2008 | Reply
Use the 3 kva transformer. It prevents overcharges.