i have a power tool that requires a 240-110 transformer ,i need help with which transformer i need to buy?
mike r asked:
the power tool says max input 2.8 kva. do i need a 3kva transformer to run this tool or is a 3 kva transformer to big. can i buy a smaller 1 kva unit that will run the tool?
Question posted courtesy of: Valerie
the power tool says max input 2.8 kva. do i need a 3kva transformer to run this tool or is a 3 kva transformer to big. can i buy a smaller 1 kva unit that will run the tool?
Question posted courtesy of: Valerie












You Ask, We Answer
February 25th, 2008 at 5:07 pm
The max size transformer it is able to handle is 2.8 kva, so buy 2.7 or smaller. Definitely dont go over, it will burn your tool out.
February 28th, 2008 at 2:57 am
3 kva. 1 kva will burn up.
I am a journeyman electrician (ret).
February 29th, 2008 at 7:36 pm
No u need to go bigger a 3kva should be ok normally they should take a 50% over load for a short time.
March 1st, 2008 at 7:27 pm
2.8 is MAX input anythang larger than that MAY burn up the tool why not be safe and buy the exact replacement transformer?
March 3rd, 2008 at 4:04 am
240v is single-phase 2-pole.
110 is single-phase 1-pole.
‘Max input’ doesn’t make any sense though - it should be ‘maximum load’. If it is going to pull 2.8kva max (usually measured with a locked rotor) then you will need a 3kva to give you sufficient power.
You might want to post more details - or contact me with them, and I can try to help you (or contact the manufacturer and see if they recommend a specific transformer - or at least give you the specs to be looking for).
March 5th, 2008 at 1:02 pm
Minimum to use is a 2.8kVA transformer - and it will run hot. This is going to be a MONSTER transformer though.
March 8th, 2008 at 11:27 pm
You should get a transformer rated for a load that is larger than the actual load, so the transformer won’t burn up.
3 kVA is a good start. Something even larger would be a bit better, but those things are expensive when you start talking about 5 kVA and up. If you can afford a 5 kVA step-down transformer, I would get that.
.
March 10th, 2008 at 7:51 am
Use the 3 kva transformer. It prevents overcharges.